Problem with ST simulated thermostat controlling my furnace
Normal control of the furnace based on temp from smart sensor
The smart sensor (xiaomi temp/hum) returns/displays in decimal degrees while the simulated thermostat(ST) displays in whole numbers. I believe the ST simulated T Stat is rounding up the decimal fro the temp sensor. This is causing the simulated T stat to go in and out of heating mode. This causes the furnace to kick on/off repeatedly and in turn throws the furnace out of sync. I tried building a piston to control this, but have had no luck.
2/15/2020, 12:17:47 AM +606ms
+1ms ╔Received event [Thermostat].thermostatOperatingState = idle with a delay of 59ms
+74ms ║RunTime Analysis CS > 19ms > PS > 5ms > PE > 50ms > CE
+77ms ║Runtime (40534 bytes) successfully initialized in 5ms (v0.3.110.20191009) (74ms)
+78ms ║╔Execution stage started
+94ms ║║Comparison (decimal) 69.0 is_greater_than_or_equal_to (decimal) 69.8 = false (1ms)
+95ms ║║Condition #2 evaluated false (14ms)
+96ms ║║Condition group #1 evaluated false (state did not change) (15ms)
+101ms ║║Comparison (enum) idle changes_to (string) heating = false (1ms)
+102ms ║║Cancelling condition #31’s schedules…
+103ms ║║Condition #31 evaluated false (6ms)
+104ms ║║Cancelling condition #25’s schedules…
+105ms ║║Condition group #25 evaluated false (state changed) (8ms)
+155ms ║║Duration 176291ms for is >= 300000ms threshold = false
+156ms ║║Comparison (enum) idle was (string) heating = false (46ms)
+157ms ║║Condition #34 evaluated false (51ms)
+158ms ║║Condition group #26 evaluated false (state did not change) (52ms)
+160ms ║║Condition group #5 evaluated true (state did not change) (0ms)
+163ms ║║Cancelling statement #16’s schedules…
+164ms ║║Condition group #16 evaluated false (state did not change) (2ms)
+166ms ║║Condition group #19 evaluated true (state did not change) (0ms)
+170ms ║║Condition group #15 evaluated true (state did not change) (0ms)
+171ms ║╚Execution stage complete. (94ms)
+172ms ╚Event processed successfully (172ms)
2/15/2020, 12:17:34 AM +404ms
+2ms ╔Received event [Thermostat].thermostatOperatingState = heating with a delay of 68ms
+10092ms ║RunTime Analysis CS > 20ms > PS > 10019ms > PE > 53ms > CE
+10093ms ║Piston waited at a semaphore for 10014ms
+10095ms ║Runtime (40619 bytes) successfully initialized in 10019ms (v0.3.110.20191009) (10092ms)
+10096ms ║╔Execution stage started
+10115ms ║║Comparison (decimal) 68.0 is_greater_than_or_equal_to (decimal) 68.8 = false (1ms)
+10116ms ║║Condition #2 evaluated false (16ms)
+10117ms ║║Condition group #1 evaluated false (state did not change) (17ms)
+10123ms ║║Comparison (enum) heating changes_to (string) heating = true (1ms)
+10124ms ║║Cancelling condition #31’s schedules…
+10125ms ║║Condition #31 evaluated true (7ms)
+10126ms ║║Cancelling condition #25’s schedules…
+10127ms ║║Condition group #25 evaluated true (state changed) (9ms)
+10129ms ║║Cancelling statement #32’s schedules…
+10136ms ║║Skipped execution of physical command [null].on([]) because it would make no change to the device. (2ms)
+10137ms ║║Executed [Furnace].on (4ms)
+10140ms ║║Condition group #15 evaluated true (state did not change) (0ms)
+10142ms ║╚Execution stage complete. (46ms)
+10143ms ╚Event processed successfully (10143ms)
2/15/2020, 12:17:34 AM +223ms
+2ms ╔Received event [Thermostat].thermostatOperatingState = idle with a delay of 64ms
+88ms ║RunTime Analysis CS > 24ms > PS > 5ms > PE > 59ms > CE
+91ms ║Runtime (40534 bytes) successfully initialized in 5ms (v0.3.110.20191009) (87ms)
+108ms ║║Comparison (decimal) 68.0 is_greater_than_or_equal_to (decimal) 68.8 = false (1ms)
+110ms ║║Condition #2 evaluated false (13ms)
+111ms ║║Condition group #1 evaluated false (state did not change) (15ms)
+116ms ║║Comparison (enum) idle changes_to (string) heating = false (1ms)
+117ms ║║Cancelling condition #31’s schedules…
+118ms ║║Condition #31 evaluated false (6ms)
+119ms ║║Cancelling condition #25’s schedules…
+120ms ║║Condition group #25 evaluated false (state changed) (9ms)
+158ms ║║Duration 177584ms for is >= 300000ms threshold = false
+159ms ║║Comparison (enum) idle was (string) heating = false (33ms)
+160ms ║║Condition #34 evaluated false (39ms)
+161ms ║║Condition group #26 evaluated false (state did not change) (40ms)
+163ms ║║Condition group #5 evaluated true (state did not change) (1ms)
+166ms ║║Cancelling statement #16’s schedules…
+167ms ║║Condition group #16 evaluated false (state did not change) (1ms)
+169ms ║║Condition group #19 evaluated true (state did not change) (1ms)
+172ms ║║Condition group #15 evaluated true (state did not change) (0ms)
+174ms ║╚Execution stage complete. (83ms)
+175ms ╚Event processed successfully (175ms)
2/15/2020, 12:17:19 AM +354ms
+1ms ╔Received event [Thermostat].thermostatOperatingState = heating with a delay of 52ms
+10087ms ║RunTime Analysis CS > 19ms > PS > 10016ms > PE > 52ms > CE
+10087ms ║Piston waited at a semaphore for 10013ms
+10090ms ║Runtime (40619 bytes) successfully initialized in 10016ms (v0.3.110.20191009) (10087ms)
+10091ms ║╔Execution stage started
+10107ms ║║Comparison (decimal) 68.0 is_greater_than_or_equal_to (decimal) 68.8 = false (1ms)
+10108ms ║║Condition #2 evaluated false (14ms)
+10109ms ║║Condition group #1 evaluated false (state did not change) (15ms)
+10114ms ║║Comparison (enum) heating changes_to (string) heating = true (1ms)
+10115ms ║║Cancelling condition #31’s schedules…
+10116ms ║║Condition #31 evaluated true (6ms)
+10117ms ║║Cancelling condition #25’s schedules…
+10118ms ║║Condition group #25 evaluated true (state changed) (8ms)
+10120ms ║║Cancelling statement #32’s schedules…
+10127ms ║║Skipped execution of physical command [null].on([]) because it would make no change to the device. (2ms)
+10128ms ║║Executed [Furnace].on (4ms)
+10131ms ║║Condition group #15 evaluated true (state did not change) (0ms)
+10133ms ║╚Execution stage complete. (43ms)
+10135ms ╚Event processed successfully (10135ms)
2/15/2020, 12:17:19 AM +196ms
+2ms ╔Received event [Thermostat].thermostatOperatingState = idle with a delay of 70ms
+80ms ║RunTime Analysis CS > 21ms > PS > 5ms > PE > 54ms > CE
+83ms ║Runtime (40536 bytes) successfully initialized in 5ms (v0.3.110.20191009) (80ms)
+101ms ║║Comparison (decimal) 68.0 is_greater_than_or_equal_to (decimal) 68.8 = false (1ms)
+102ms ║║Condition #2 evaluated false (15ms)
+103ms ║║Condition group #1 evaluated false (state did not change) (16ms)
+108ms ║║Comparison (enum) idle changes_to (string) heating = false (1ms)
+109ms ║║Condition #31 evaluated false (5ms)
+110ms ║║Condition group #25 evaluated false (state did not change) (6ms)
+232ms ║║Duration 177468ms for is >= 300000ms threshold = false
+232ms ║║Comparison (enum) idle was (string) heating = false (117ms)
+234ms ║║Condition #34 evaluated false (123ms)
+235ms ║║Condition group #26 evaluated false (state did not change) (123ms)
+237ms ║║Condition group #5 evaluated true (state did not change) (1ms)
+240ms ║║Cancelling statement #16’s schedules…
+241ms ║║Condition group #16 evaluated false (state did not change) (2ms)
+243ms ║║Condition group #19 evaluated true (state did not change) (0ms)
+247ms ║║Condition group #15 evaluated true (state did not change) (0ms)
+248ms ║╚Execution stage complete. (165ms)
+249ms ╚Event processed successfully (249ms)
2/15/2020, 12:17:04 AM +299ms
+0ms ╔Received event [Thermostat].thermostatOperatingState = heating with a delay of 47ms
+70ms ║RunTime Analysis CS > 14ms > PS > 6ms > PE > 51ms > CE
+72ms ║Runtime (40537 bytes) successfully initialized in 6ms (v0.3.110.20191009) (71ms)
+90ms ║║Comparison (decimal) 68.0 is_greater_than_or_equal_to (decimal) 68.8 = false (2ms)
+91ms ║║Cancelling condition #2’s schedules…
+92ms ║║Condition #2 evaluated false (15ms)
+93ms ║║Cancelling condition #1’s schedules…
+94ms ║║Condition group #1 evaluated false (state changed) (17ms)
+99ms ║║Comparison (enum) heating changes_to (string) heating = false (1ms)
+100ms ║║Condition #31 evaluated false (5ms)
+101ms ║║Condition group #25 evaluated false (state did not change) (6ms)
+154ms ║║Duration 177502ms for is >= 300000ms threshold = false
+155ms ║║Comparison (enum) heating was (string) heating = false (49ms)
+157ms ║║Condition #34 evaluated false (54ms)
+157ms ║║Condition group #26 evaluated false (state did not change) (55ms)
+164ms ║║Condition group #16 evaluated false (state did not change) (1ms)
+166ms ║║Condition group #19 evaluated true (state did not change) (1ms)
+169ms ║║Condition group #15 evaluated true (state did not change) (0ms)
+171ms ║╚Execution stage complete. (98ms)
+172ms ╚Event processed successfully (173ms)
2/15/2020, 12:17:04 AM +137ms
+0ms ╔Received event [Thermostat].thermostatOperatingState = idle with a delay of 41ms
+68ms ║RunTime Analysis CS > 14ms > PS > 6ms > PE > 49ms > CE
+71ms ║Runtime (40536 bytes) successfully initialized in 6ms (v0.3.110.20191009) (70ms)
+72ms ║╔Execution stage started
+88ms ║║Comparison (decimal) 69.0 is_greater_than_or_equal_to (decimal) 68.8 = true (2ms)
+89ms ║║Cancelling condition #2’s schedules…
+90ms ║║Condition #2 evaluated true (14ms)
+91ms ║║Cancelling condition #1’s schedules…
+92ms ║║Condition group #1 evaluated true (state changed) (17ms)
+94ms ║║Cancelling statement #3’s schedules…
+102ms ║║Skipped execution of physical command [null].setThermostatMode([heat]) because it would make no change to the device. (3ms)
+103ms ║║Executed [Thermostat].setThermostatMode (5ms)
+106ms ║║Condition group #15 evaluated true (state did not change) (1ms)
+108ms ║╚Execution stage complete. (36ms)
+109ms ╚Event processed successfully (109ms)
2/15/2020, 12:16:49 AM +425ms
+1ms ╔Received event [Thermostat].thermostatOperatingState = heating with a delay of 74ms
+79ms ║RunTime Analysis CS > 21ms > PS > 5ms > PE > 53ms > CE
+82ms ║Runtime (40537 bytes) successfully initialized in 5ms (v0.3.110.20191009) (79ms)
+100ms ║║Comparison (decimal) 68.0 is_greater_than_or_equal_to (decimal) 68.8 = false (1ms)
+102ms ║║Cancelling condition #2’s schedules…
+103ms ║║Cancelling condition #1’s schedules…
+104ms ║║Condition group #1 evaluated false (state changed) (17ms)
+109ms ║║Comparison (enum) heating changes_to (string) heating = false (0ms)
+111ms ║║Condition #31 evaluated false (6ms)
+112ms ║║Condition group #25 evaluated false (state did not change) (7ms)
+245ms ║║Duration 177521ms for is >= 300000ms threshold = false
+246ms ║║Comparison (enum) heating was (string) heating = false (129ms)
+248ms ║║Condition #34 evaluated false (134ms)
+249ms ║║Condition group #26 evaluated false (state did not change) (136ms)
+251ms ║║Condition group #5 evaluated true (state did not change) (1ms)
+254ms ║║Cancelling statement #16’s schedules…
+255ms ║║Condition group #16 evaluated false (state did not change) (2ms)
+257ms ║║Condition group #19 evaluated true (state did not change) (0ms)
+260ms ║║Condition group #15 evaluated true (state did not change) (0ms)
+262ms ║╚Execution stage complete. (180ms)
+263ms ╚Event processed successfully (263ms)
2/15/2020, 12:16:49 AM +215ms
+2ms ╔Received event [Thermostat].thermostatOperatingState = idle with a delay of 57ms
+77ms ║RunTime Analysis CS > 19ms > PS > 5ms > PE > 53ms > CE
+79ms ║Runtime (40536 bytes) successfully initialized in 5ms (v0.3.110.20191009) (77ms)
+96ms ║║Comparison (decimal) 69.0 is_greater_than_or_equal_to (decimal) 68.8 = true (1ms)
+97ms ║║Cancelling condition #2’s schedules…
+98ms ║║Condition #2 evaluated true (14ms)
+99ms ║║Cancelling condition #1’s schedules…
+100ms ║║Condition group #1 evaluated true (state changed) (16ms)
+102ms ║║Cancelling statement #3’s schedules…
+109ms ║║Skipped execution of physical command [null].setThermostatMode([heat]) because it would make no change to the device. (3ms)
+110ms ║║Executed [Thermostat].setThermostatMode (4ms)
+113ms ║║Condition group #15 evaluated true (state did not change) (0ms)
+115ms ║╚Execution stage complete. (35ms)
+116ms ╚Event processed successfully (116ms)
2/15/2020, 12:16:34 AM +516ms
+1ms ╔Received event [Thermostat].thermostatOperatingState = heating with a delay of 59ms
+75ms ║RunTime Analysis CS > 21ms > PS > 5ms > PE > 50ms > CE
+77ms ║Runtime (40535 bytes) successfully initialized in 5ms (v0.3.110.20191009) (75ms)
+95ms ║║Comparison (decimal) 68.0 is_greater_than_or_equal_to (decimal) 68.8 = false (1ms)
+98ms ║║Condition #2 evaluated false (15ms)
+98ms ║║Cancelling condition #1’s schedules…
+99ms ║║Condition group #1 evaluated false (state changed) (17ms)
+104ms ║║Comparison (enum) heating changes_to (string) heating = false (0ms)
+106ms ║║Cancelling condition #31’s schedules…
+106ms ║║Condition #31 evaluated false (6ms)
+107ms ║║Cancelling condition #25’s schedules…
+108ms ║║Condition group #25 evaluated false (state changed) (8ms)
+148ms ║║Duration 177476ms for is >= 300000ms threshold = false
+149ms ║║Comparison (enum) heating was (string) heating = false (36ms)
+150ms ║║Condition #34 evaluated false (41ms)
+151ms ║║Condition group #26 evaluated false (state did not change) (42ms)
+153ms ║║Condition group #5 evaluated true (state did not change) (0ms)
+156ms ║║Cancelling statement #16’s schedules…
+157ms ║║Condition group #16 evaluated false (state did not change) (2ms)
+159ms ║║Condition group #19 evaluated true (state did not change) (0ms)
+163ms ║║Condition group #15 evaluated true (state did not change) (0ms)
+165ms ║╚Execution stage complete. (86ms)
+166ms ╚Event processed successfully (165ms)
2/15/2020, 12:16:34 AM +230ms
+1ms ╔Received event [Thermostat].thermostatOperatingState = idle with a delay of 54ms
+72ms ║RunTime Analysis CS > 19ms > PS > 5ms > PE > 47ms > CE
+74ms ║Runtime (40534 bytes) successfully initialized in 5ms (v0.3.110.20191009) (72ms)
+75ms ║╔Execution stage started
+91ms ║║Comparison (decimal) 69.0 is_greater_than_or_equal_to (decimal) 68.8 = true (1ms)
+93ms ║║Cancelling condition #2’s schedules…
+94ms ║║Condition #2 evaluated true (14ms)
+95ms ║║Cancelling condition #1’s schedules…
+95ms ║║Condition group #1 evaluated true (state changed) (17ms)
+98ms ║║Cancelling statement #3’s schedules…
+105ms ║║Skipped execution of physical command [null].setThermostatMode([heat]) because it would make no change to the device. (3ms)
+106ms ║║Executed [Thermostat].setThermostatMode (4ms)
+109ms ║║Condition group #15 evaluated true (state did not change) (0ms)
+110ms ║╚Execution stage complete. (36ms)
+111ms ╚Event processed successfully (111ms)
2/15/2020, 12:16:19 AM +321ms
+0ms ╔Received event [Thermostat].thermostatOperatingState = heating with a delay of 44ms
+10080ms ║RunTime Analysis CS > 14ms > PS > 10016ms > PE > 51ms > CE
+10081ms ║Piston waited at a semaphore for 10013ms
+10083ms ║Runtime (40619 bytes) successfully initialized in 10016ms (v0.3.110.20191009) (10082ms)
+10084ms ║╔Execution stage started
+10100ms ║║Comparison (decimal) 68.0 is_greater_than_or_equal_to (decimal) 68.8 = false (1ms)
+10102ms ║║Condition #2 evaluated false (13ms)
+10103ms ║║Condition group #1 evaluated false (state did not change) (14ms)
+10363ms ║║Comparison (enum) heating changes_to (string) heating = true (1ms)
+10365ms ║║Cancelling condition #31’s schedules…
+10367ms ║║Condition #31 evaluated true (262ms)
+10368ms ║║Cancelling condition #25’s schedules…
+10369ms ║║Condition group #25 evaluated true (state changed) (266ms)
+10372ms ║║Cancelling statement #32’s schedules…
+10382ms ║║Skipped execution of physical command [null].on([]) because it would make no change to the device. (2ms)
+10382ms ║║Executed [Furnace].on (5ms)
+10385ms ║║Condition group #15 evaluated true (state did not change) (0ms)
+10387ms ║╚Execution stage complete. (303ms)
+10388ms ╚Event processed successfully (10388ms)
2/15/2020, 12:16:19 AM +188ms
+1ms ╔Received event [Thermostat].thermostatOperatingState = idle with a delay of 51ms
+68ms ║RunTime Analysis CS > 17ms > PS > 3ms > PE > 48ms > CE
+71ms ║Runtime (40536 bytes) successfully initialized in 3ms (v0.3.110.20191009) (68ms)
+88ms ║║Comparison (decimal) 68.0 is_greater_than_or_equal_to (decimal) 68.8 = false (1ms)
+89ms ║║Condition #2 evaluated false (13ms)
+90ms ║║Condition group #1 evaluated false (state did not change) (15ms)
+95ms ║║Comparison (enum) idle changes_to (string) heating = false (0ms)
+97ms ║║Condition #31 evaluated false (5ms)
+98ms ║║Condition group #25 evaluated false (state did not change) (6ms)
+155ms ║║Duration 177481ms for is >= 300000ms threshold = false
+156ms ║║Comparison (enum) idle was (string) heating = false (53ms)
+157ms ║║Condition #34 evaluated false (59ms)
+158ms ║║Condition group #26 evaluated false (state did not change) (60ms)
+170ms ║║Condition group #15 evaluated true (state did not change) (1ms)
+171ms ║╚Execution stage complete. (100ms)
2/15/2020, 12:16:04 AM +333ms
+1ms ╔Received event [Thermostat].thermostatOperatingState = heating with a delay of 63ms
+89ms ║RunTime Analysis CS > 21ms > PS > 4ms > PE > 64ms > CE
+91ms ║Runtime (40535 bytes) successfully initialized in 4ms (v0.3.110.20191009) (89ms)
+109ms ║║Comparison (decimal) 68.0 is_greater_than_or_equal_to (decimal) 68.8 = false (2ms)
+110ms ║║Cancelling condition #2’s schedules…
+111ms ║║Condition #2 evaluated false (14ms)
+112ms ║║Cancelling condition #1’s schedules…
+113ms ║║Condition group #1 evaluated false (state changed) (17ms)
+118ms ║║Comparison (enum) heating changes_to (string) heating = false (1ms)
+119ms ║║Cancelling condition #31’s schedules…
+120ms ║║Condition #31 evaluated false (6ms)
+121ms ║║Cancelling condition #25’s schedules…
+122ms ║║Condition group #25 evaluated false (state changed) (8ms)
+188ms ║║Duration 177455ms for is >= 300000ms threshold = false
+189ms ║║Comparison (enum) heating was (string) heating = false (62ms)
+191ms ║║Condition #34 evaluated false (67ms)
+192ms ║║Condition group #26 evaluated false (state did not change) (68ms)
+194ms ║║Condition group #5 evaluated true (state did not change) (0ms)
+197ms ║║Cancelling statement #16’s schedules…
+198ms ║║Condition group #16 evaluated false (state did not change) (2ms)
+201ms ║║Condition group #19 evaluated true (state did not change) (1ms)
+204ms ║║Condition group #15 evaluated true (state did not change) (0ms)
+206ms ║╚Execution stage complete. (114ms)
+207ms ╚Event processed successfully (207ms)
2/15/2020, 12:16:04 AM +143ms
+1ms ╔Received event [Thermostat].thermostatOperatingState = idle with a delay of 38ms
+80ms ║RunTime Analysis CS > 24ms > PS > 3ms > PE > 52ms > CE
+82ms ║Runtime (40534 bytes) successfully initialized in 3ms (v0.3.110.20191009) (80ms)
+100ms ║║Comparison (decimal) 69.0 is_greater_than_or_equal_to (decimal) 68.8 = true (2ms)
+101ms ║║Cancelling condition #2’s schedules…
+102ms ║║Condition #2 evaluated true (15ms)
+104ms ║║Condition group #1 evaluated true (state changed) (17ms)
+106ms ║║Cancelling statement #3’s schedules…
+113ms ║║Skipped execution of physical command [null].setThermostatMode([heat]) because it would make no change to the device. (3ms)
+114ms ║║Executed [Thermostat].setThermostatMode (5ms)
+117ms ║║Condition group #15 evaluated true (state did not change) (0ms)
+119ms ║╚Execution stage complete. (36ms)
+120ms ╚Event processed successfully (120ms)
2/15/2020, 12:15:49 AM +434ms
+1ms ╔Received event [Thermostat].thermostatOperatingState = heating with a delay of 58ms
+10084ms ║RunTime Analysis CS > 14ms > PS > 10021ms > PE > 49ms > CE
+10085ms ║Piston waited at a semaphore for 10017ms
+10088ms ║Runtime (40619 bytes) successfully initialized in 10021ms (v0.3.110.20191009) (10086ms)
+10088ms ║╔Execution stage started
+10105ms ║║Comparison (decimal) 68.0 is_greater_than_or_equal_to (decimal) 68.8 = false (1ms)
+10106ms ║║Condition #2 evaluated false (14ms)
+10107ms ║║Condition group #1 evaluated false (state did not change) (15ms)
+10112ms ║║Comparison (enum) heating changes_to (string) heating = true (1ms)
+10113ms ║║Cancelling condition #31’s schedules…
+10114ms ║║Condition #31 evaluated true (6ms)
+10115ms ║║Cancelling condition #25’s schedules…
+10116ms ║║Condition group #25 evaluated true (state changed) (8ms)
+10118ms ║║Cancelling statement #32’s schedules…
+10125ms ║║Skipped execution of physical command [null].on([]) because it would make no change to the device. (2ms)
+10126ms ║║Executed [Furnace].on (4ms)
+10128ms ║║Condition group #15 evaluated true (state did not change) (0ms)
+10130ms ║╚Execution stage complete. (42ms)
+10131ms ╚Event processed successfully (10131ms)
2/15/2020, 12:15:49 AM +263ms
+75ms ║RunTime Analysis CS > 19ms > PS > 5ms > PE > 51ms > CE
+77ms ║Runtime (40534 bytes) successfully initialized in 5ms (v0.3.110.20191009) (75ms)
+96ms ║║Comparison (decimal) 68.0 is_greater_than_or_equal_to (decimal) 68.8 = false (1ms)
+99ms ║║Condition group #1 evaluated false (state did not change) (16ms)
+104ms ║║Comparison (enum) idle changes_to (string) heating = false (0ms)
+105ms ║║Cancelling condition #31’s schedules…
+106ms ║║Condition #31 evaluated false (7ms)
+145ms ║║Duration 177491ms for is >= 300000ms threshold = false
+146ms ║║Comparison (enum) idle was (string) heating = false (34ms)
+147ms ║║Condition #34 evaluated false (38ms)
+148ms ║║Condition group #26 evaluated false (state did not change) (40ms)
+150ms ║║Condition group #5 evaluated true (state did not change) (0ms)
+153ms ║║Cancelling statement #16’s schedules…
+154ms ║║Condition group #16 evaluated false (state did not change) (2ms)
+157ms ║║Condition group #19 evaluated true (state did not change) (0ms)
+160ms ║║Condition group #15 evaluated true (state did not change) (1ms)
+162ms ║╚Execution stage complete. (83ms)
+163ms ╚Event processed successfully (163ms)
2/15/2020, 12:15:34 AM +346ms
+2ms ╔Received event [Thermostat].thermostatOperatingState = heating with a delay of 93ms
+10118ms ║RunTime Analysis CS > 23ms > PS > 10022ms > PE > 72ms > CE
+10119ms ║Piston waited at a semaphore for 10018ms
+10121ms ║Runtime (40619 bytes) successfully initialized in 10022ms (v0.3.110.20191009) (10118ms)
+10122ms ║╔Execution stage started
+10149ms ║║Comparison (decimal) 68.0 is_greater_than_or_equal_to (decimal) 68.8 = false (1ms)
+10150ms ║║Condition #2 evaluated false (23ms)
+10151ms ║║Condition group #1 evaluated false (state did not change) (24ms)
+10156ms ║║Comparison (enum) heating changes_to (string) heating = true (1ms)
+10157ms ║║Cancelling condition #31’s schedules…
+10158ms ║║Condition #31 evaluated true (6ms)
+10159ms ║║Cancelling condition #25’s schedules…
+10160ms ║║Condition group #25 evaluated true (state changed) (8ms)
+10162ms ║║Cancelling statement #32’s schedules…
+10170ms ║║Skipped execution of physical command [null].on([]) because it would make no change to the device. (2ms)
+10170ms ║║Executed [Furnace].on (4ms)
+10173ms ║║Condition group #15 evaluated true (state did not change) (0ms)
+10175ms ║╚Execution stage complete. (53ms)
+10176ms ╚Event processed successfully (10176ms)
2/15/2020, 12:15:34 AM +163ms
+1ms ╔Received event [Thermostat].thermostatOperatingState = idle with a delay of 63ms
+72ms ║RunTime Analysis CS > 18ms > PS > 5ms > PE > 48ms > CE
+93ms ║║Comparison (decimal) 68.0 is_greater_than_or_equal_to (decimal) 68.8 = false (1ms)
+94ms ║║Condition #2 evaluated false (15ms)
+95ms ║║Condition group #1 evaluated false (state did not change) (16ms)
+100ms ║║Comparison (enum) idle changes_to (string) heating = false (0ms)
+102ms ║║Condition #31 evaluated false (6ms)
+103ms ║║Cancelling condition #25’s schedules…
+104ms ║║Condition group #25 evaluated false (state changed) (8ms)
+216ms ║║Duration 177376ms for is >= 300000ms threshold = false
+216ms ║║Comparison (enum) idle was (string) heating = false (107ms)
+218ms ║║Condition #34 evaluated false (113ms)
+219ms ║║Condition group #26 evaluated false (state did not change) (114ms)
+221ms ║║Condition group #5 evaluated true (state did not change) (0ms)
+224ms ║║Cancelling statement #16’s schedules…
+225ms ║║Condition group #16 evaluated false (state did not change) (2ms)
+228ms ║║Condition group #19 evaluated true (state did not change) (1ms)
+231ms ║║Condition group #15 evaluated true (state did not change) (0ms)
+233ms ║╚Execution stage complete. (159ms)
+234ms ╚Event processed successfully (234ms)
2/15/2020, 12:15:19 AM +429ms
+2ms ╔Received event [Thermostat].thermostatOperatingState = heating with a delay of 60ms
+9914ms ║RunTime Analysis CS > 17ms > PS > 9846ms > PE > 51ms > CE
+9915ms ║Piston waited at a semaphore for 9842ms
+9918ms ║Runtime (40613 bytes) successfully initialized in 9846ms (v0.3.110.20191009) (9915ms)
+9918ms ║╔Execution stage started
+9935ms ║║Comparison (decimal) 68.0 is_greater_than_or_equal_to (decimal) 68.8 = false (1ms)
+9937ms ║║Condition #2 evaluated false (14ms)
+9937ms ║║Condition group #1 evaluated false (state did not change) (15ms)
+9942ms ║║Comparison (enum) heating changes_to (string) heating = true (0ms)
+9944ms ║║Cancelling condition #31’s schedules…
+9945ms ║║Condition #31 evaluated true (7ms)
+9946ms ║║Cancelling condition #25’s schedules…
+9947ms ║║Condition group #25 evaluated true (state changed) (8ms)
+9948ms ║║Cancelling statement #32’s schedules…
+9956ms ║║Skipped execution of physical command [null].on([]) because it would make no change to the device. (3ms)
+9957ms ║║Executed [Furnace].on (5ms)
+9960ms ║║Condition group #15 evaluated true (state did not change) (0ms)
+9961ms ║╚Execution stage complete. (43ms)
+9962ms ╚Event processed successfully (9962ms)
2/15/2020, 12:15:19 AM +258ms
+2ms ╔Received event [Thermostat].thermostatOperatingState = idle with a delay of 65ms
+80ms ║RunTime Analysis CS > 23ms > PS > 5ms > PE > 52ms > CE
+83ms ║Runtime (40534 bytes) successfully initialized in 5ms (v0.3.110.20191009) (81ms)
+102ms ║║Comparison (decimal) 68.0 is_greater_than_or_equal_to (decimal) 68.8 = false (1ms)
+103ms ║║Condition #2 evaluated false (15ms)
+104ms ║║Condition group #1 evaluated false (state did not change) (16ms)
+109ms ║║Comparison (enum) idle changes_to (string) heating = false (0ms)
+111ms ║║Cancelling condition #31’s schedules…
+112ms ║║Condition #31 evaluated false (6ms)
+113ms ║║Cancelling condition #25’s schedules…
+113ms ║║Condition group #25 evaluated false (state changed) (8ms)
+177ms ║║Duration 177435ms for is >= 300000ms threshold = false
+178ms ║║Comparison (enum) idle was (string) heating = false (60ms)
+180ms ║║Condition #34 evaluated false (65ms)
+180ms ║║Condition group #26 evaluated false (state did not change) (66ms)
+183ms ║║Condition group #5 evaluated true (state did not change) (1ms)
+186ms ║║Cancelling statement #16’s schedules…
+187ms ║║Condition group #16 evaluated false (state did not change) (2ms)
+189ms ║║Condition group #19 evaluated true (state did not change) (0ms)
+192ms ║║Condition group #15 evaluated true (state did not change) (0ms)
+194ms ║╚Execution stage complete. (111ms)
+195ms ╚Event processed successfully (195ms)
2/15/2020, 12:15:04 AM +365ms
+1ms ╔Received event [Thermostat].thermostatOperatingState = heating with a delay of 67ms
+10102ms ║RunTime Analysis CS > 19ms > PS > 10026ms > PE > 56ms > CE
+10103ms ║Piston waited at a semaphore for 10022ms
+10105ms ║Runtime (40619 bytes) successfully initialized in 10026ms (v0.3.110.20191009) (10103ms)
+10106ms ║╔Execution stage started
+10122ms ║║Comparison (decimal) 68.0 is_greater_than_or_equal_to (decimal) 68.8 = false (1ms)
+10124ms ║║Condition #2 evaluated false (13ms)
+10125ms ║║Condition group #1 evaluated false (state did not change) (15ms)
+10130ms ║║Comparison (enum) heating changes_to (string) heating = true (0ms)
+10131ms ║║Cancelling condition #31’s schedules…
+10132ms ║║Condition #31 evaluated true (6ms)
+10133ms ║║Cancelling condition #25’s schedules…
+10134ms ║║Condition group #25 evaluated true (state changed) (9ms)
+10136ms ║║Cancelling statement #32’s schedules…
+10143ms ║║Skipped execution of physical command [null].on([]) because it would make no change to the device. (2ms)
+10144ms ║║Executed [Furnace].on (4ms)
+10147ms ║║Condition group #15 evaluated true (state did not change) (1ms)
+10148ms ║╚Execution stage complete. (43ms)
+10149ms ╚Event processed successfully (10149ms)
2/15/2020, 12:15:04 AM +217ms
+1ms ╔Received event [Thermostat].thermostatOperatingState = idle with a delay of 135ms
+81ms ║RunTime Analysis CS > 22ms > PS > 6ms > PE > 53ms > CE
+83ms ║Runtime (40535 bytes) successfully initialized in 6ms (v0.3.110.20191009) (81ms)
+103ms ║║Comparison (decimal) 68.0 is_greater_than_or_equal_to (decimal) 68.8 = false (1ms)
+104ms ║║Condition #2 evaluated false (16ms)
+105ms ║║Condition group #1 evaluated false (state did not change) (18ms)
+110ms ║║Comparison (enum) idle changes_to (string) heating = false (1ms)
+114ms ║║Condition group #25 evaluated false (state changed) (8ms)
+173ms ║║Duration 177491ms for is >= 300000ms threshold = false
+173ms ║║Comparison (enum) idle was (string) heating = false (55ms)
+175ms ║║Condition #34 evaluated false (59ms)
+176ms ║║Condition group #26 evaluated false (state did not change) (61ms)
+178ms ║║Condition group #5 evaluated true (state did not change) (1ms)
+181ms ║║Cancelling statement #16’s schedules…
+181ms ║║Condition group #16 evaluated false (state did not change) (1ms)
+184ms ║║Condition group #19 evaluated true (state did not change) (1ms)
+187ms ║║Condition group #15 evaluated true (state did not change) (1ms)
+188ms ║╚Execution stage complete. (104ms)
+189ms ╚Event processed successfully (189ms)
2/15/2020, 12:14:49 AM +318ms
+2ms ╔Received event [Thermostat].thermostatOperatingState = heating with a delay of 64ms
+10148ms ║RunTime Analysis CS > 19ms > PS > 10073ms > PE > 56ms > CE
+10149ms ║Piston waited at a semaphore for 10069ms
+10151ms ║Runtime (40619 bytes) successfully initialized in 10073ms (v0.3.110.20191009) (10149ms)
+10152ms ║╔Execution stage started
+10171ms ║║Comparison (decimal) 68.0 is_greater_than_or_equal_to (decimal) 68.8 = false (1ms)
+10172ms ║║Condition #2 evaluated false (16ms)
+10173ms ║║Condition group #1 evaluated false (state did not change) (17ms)
+10178ms ║║Comparison (enum) heating changes_to (string) heating = true (1ms)
+10180ms ║║Cancelling condition #31’s schedules…
+10180ms ║║Condition #31 evaluated true (6ms)
+10181ms ║║Cancelling condition #25’s schedules…
+10182ms ║║Condition group #25 evaluated true (state changed) (8ms)
+10184ms ║║Cancelling statement #32’s schedules…
+10191ms ║║Skipped execution of physical command [null].on([]) because it would make no change to the device. (2ms)
+10192ms ║║Executed [Furnace].on (4ms)
+10195ms ║║Condition group #15 evaluated true (state did not change) (1ms)
+10197ms ║╚Execution stage complete. (44ms)
+10198ms ╚Event processed successfully (10198ms)
2/15/2020, 12:14:49 AM +144ms
+2ms ╔Received event [Thermostat].thermostatOperatingState = idle with a delay of 60ms
+83ms ║RunTime Analysis CS > 27ms > PS > 5ms > PE > 51ms > CE
+85ms ║Runtime (40534 bytes) successfully initialized in 5ms (v0.3.110.20191009) (83ms)
+86ms ║╔Execution stage started
+104ms ║║Comparison (decimal) 68.0 is_greater_than_or_equal_to (decimal) 68.8 = false (1ms)
+105ms ║║Condition #2 evaluated false (15ms)
+106ms ║║Condition group #1 evaluated false (state did not change) (16ms)
+112ms ║║Comparison (enum) idle changes_to (string) heating = false (0ms)
+113ms ║║Cancelling condition #31’s schedules…
+114ms ║║Condition #31 evaluated false (7ms)
+115ms ║║Cancelling condition #25’s schedules…
+116ms ║║Condition group #25 evaluated false (state changed) (9ms)
+185ms ║║Duration 177362ms for is >= 300000ms threshold = false
+186ms ║║Comparison (enum) idle was (string) heating = false (65ms)
+188ms ║║Condition #34 evaluated false (71ms)
+189ms ║║Condition group #26 evaluated false (state did not change) (73ms)
+192ms ║║Condition group #5 evaluated true (state did not change) (0ms)
+196ms ║║Cancelling statement #16’s schedules…
+197ms ║║Condition group #16 evaluated false (state did not change) (2ms)
+200ms ║║Condition group #19 evaluated true (state did not change) (0ms)
+207ms ║╚Execution stage complete. (121ms)
+208ms ╚Event processed successfully (208ms)
2/15/2020, 12:14:34 AM +649ms
+1ms ╔Received event [Thermostat].thermostatOperatingState = heating with a delay of 68ms
+9692ms ║RunTime Analysis CS > 24ms > PS > 9611ms > PE > 58ms > CE
+9693ms ║Piston waited at a semaphore for 9606ms
+9695ms ║Runtime (40613 bytes) successfully initialized in 9611ms (v0.3.110.20191009) (9693ms)
+9696ms ║╔Execution stage started
+9713ms ║║Comparison (decimal) 68.0 is_greater_than_or_equal_to (decimal) 68.8 = false (1ms)
+9714ms ║║Condition #2 evaluated false (14ms)
+9715ms ║║Condition group #1 evaluated false (state did not change) (15ms)
+9720ms ║║Comparison (enum) heating changes_to (string) heating = true (1ms)
+9722ms ║║Cancelling condition #31’s schedules…
+9722ms ║║Condition #31 evaluated true (6ms)
+9723ms ║║Cancelling condition #25’s schedules…
+9724ms ║║Condition group #25 evaluated true (state changed) (8ms)
+9726ms ║║Cancelling statement #32’s schedules…
+9734ms ║║Skipped execution of physical command [null].on([]) because it would make no change to the device. (3ms)
+9735ms ║║Executed [Furnace].on (5ms)
+9738ms ║║Condition group #15 evaluated true (state did not change) (1ms)
+9739ms ║╚Execution stage complete. (43ms)
+9740ms ╚Event processed successfully (9740ms)
2/15/2020, 12:14:34 AM +251ms
+1ms ╔Received event [Thermostat].thermostatOperatingState = idle with a delay of 49ms
+77ms ║RunTime Analysis CS > 16ms > PS > 4ms > PE > 57ms > CE
+80ms ║Runtime (40536 bytes) successfully initialized in 4ms (v0.3.110.20191009) (77ms)
+324ms ║║Comparison (decimal) 68.0 is_greater_than_or_equal_to (decimal) 68.8 = false (1ms)
+326ms ║║Condition #2 evaluated false (241ms)
+327ms ║║Condition group #1 evaluated false (state did not change) (242ms)
+333ms ║║Comparison (enum) idle changes_to (string) heating = false (1ms)
+334ms ║║Condition #31 evaluated false (6ms)
+335ms ║║Condition group #25 evaluated false (state did not change) (7ms)
+462ms ║║Duration 177674ms for is >= 300000ms threshold = false
+463ms ║║Comparison (enum) idle was (string) heating = false (122ms)
+465ms ║║Condition #34 evaluated false (127ms)
+465ms ║║Condition group #26 evaluated false (state did not change) (129ms)
+468ms ║║Condition group #5 evaluated true (state did not change) (0ms)
+471ms ║║Cancelling statement #16’s schedules…
+472ms ║║Condition group #16 evaluated false (state did not change) (1ms)
+474ms ║║Condition group #19 evaluated true (state did not change) (1ms)
+477ms ║║Condition group #15 evaluated true (state did not change) (0ms)
+479ms ║╚Execution stage complete. (399ms)
+480ms ╚Event processed successfully (480ms)
2/15/2020, 12:14:19 AM +529ms
+2ms ╔Received event [Thermostat].thermostatOperatingState = heating with a delay of 69ms
+83ms ║RunTime Analysis CS > 19ms > PS > 6ms > PE > 58ms > CE
+86ms ║Runtime (40535 bytes) successfully initialized in 6ms (v0.3.110.20191009) (82ms)
+87ms ║╔Execution stage started
+105ms ║║Cancelling condition #2’s schedules…
+106ms ║║Condition #2 evaluated false (14ms)
+107ms ║║Cancelling condition #1’s schedules…
+108ms ║║Condition group #1 evaluated false (state changed) (17ms)
+119ms ║║Comparison (enum) heating changes_to (string) heating = false (0ms)
+120ms ║║Cancelling condition #31’s schedules…
+123ms ║║Condition #31 evaluated false (8ms)
+124ms ║║Cancelling condition #25’s schedules…
+125ms ║║Condition group #25 evaluated false (state changed) (11ms)
+172ms ║║Duration 177745ms for is >= 300000ms threshold = false
+173ms ║║Comparison (enum) heating was (string) heating = false (43ms)
+174ms ║║Condition #34 evaluated false (48ms)
+175ms ║║Condition group #26 evaluated false (state did not change) (49ms)
+182ms ║║Condition group #16 evaluated false (state did not change) (2ms)
+185ms ║║Condition group #19 evaluated true (state did not change) (1ms)
+190ms ║║Condition group #15 evaluated true (state did not change) (1ms)
+192ms ║╚Execution stage complete. (106ms)
+193ms ╚Event processed successfully (193ms)
2/15/2020, 12:14:19 AM +234ms
+1ms ╔Received event [Thermostat].thermostatOperatingState = idle with a delay of 57ms
+85ms ║RunTime Analysis CS > 16ms > PS > 5ms > PE > 64ms > CE
+88ms ║Runtime (40534 bytes) successfully initialized in 5ms (v0.3.110.20191009) (86ms)
+106ms ║║Comparison (decimal) 69.0 is_greater_than_or_equal_to (decimal) 68.8 = true (2ms)
+108ms ║║Cancelling condition #2’s schedules…
+108ms ║║Condition #2 evaluated true (15ms)
+109ms ║║Cancelling condition #1’s schedules…
+110ms ║║Condition group #1 evaluated true (state changed) (17ms)
+112ms ║║Cancelling statement #3’s schedules…
+119ms ║║Skipped execution of physical command [null].setThermostatMode([heat]) because it would make no change to the device. (2ms)
+120ms ║║Executed [Thermostat].setThermostatMode (4ms)
+123ms ║║Condition group #15 evaluated true (state did not change) (0ms)
+125ms ║╚Execution stage complete. (37ms)
+126ms ╚Event processed successfully (126ms)
2/15/2020, 12:14:04 AM +316ms